Why am I getting negative kWh savings on an Min OA reduction measure for a PSZ?

720-306-1742      support@optimiserenergy.com

Home Forums Commercial Why am I getting negative kWh savings on an Min OA reduction measure for a PSZ?

This topic contains 1 reply, has 1 voice, and was last updated by  Gamaliel Lodge 3 weeks ago.

  • Author
    Posts
  • #8530

    Gamaliel Lodge
    Keymaster

    I use the Min OA Flow measure on PSZ to reduced the minimum outside area ratio. This measure resulted in negative kWh savings for cooling. How is that possible?

    #8531

    Gamaliel Lodge
    Keymaster

    The min OA reduction will typically produce positive savings only if there is an existing economizer that is functioning. However, for package units we have the economizer disabled by default. We have made this decision based on the field experience of our engineers, looking into operation conditions of various package units, retrofitting package units, and doing control programming for package units. You would be surprised at the amount of packages units with economizer failure (outside air damper locked up) or economizer control not even hooked up or enabled, especially for small units.

    If you are sure the economizer is working for your package units, you may enable the economizer (in the System Specifications frame) and set the economizer temperature limit to be a reasonably high value, say 72F. Doing this should produce positive electric savings, but you may have to re-calibrate the baseline model.

Viewing 2 posts - 1 through 2 (of 2 total)