    How do I model and indirect or sidearm water heater with a boiler?

    #4219
    Ryan Moore
    Keymaster

    There is a simple method to use for this answer if the tank fits into the assumptions listed. Then, there is a more complicated answer if the tank is significantly different. See the 2 different methods below:

    Here is a simple workaround for sidearm heaters, based on support documentation for EERE standards:

    Assumptions:

    40 gal metal tank
    1 in. (2.56 cm) of HFC-245fa insulation
    intermittent pilot ignition device

    Procedure:

    Set Recovery Eff (RE) to system efficiency of boiler
    Set EF = .65*RE + 12.6

    Here is the more complicated workaround:

    Select a standard tank water heater.
    Set the tank size and btu/hr capacity
    Set the Recovery Efficiency to the AFUE of the heating system boiler
    Use the attached worksheet to estimate the EF
    Enter tank size
    Enter boiler AFUE for Thermal Efficiency
    Estimate thermal losses for the tank as Btu/hr or %/hr (percent of difference between ambient and tank temperatures)
    The %/hr could be measured directly as follows:
    Measure hot water temp=Ti
    Turn off heat source for 1 hour
    Measure hot water temp=Tf
    %/hr = 100*(Ti-Tf)/(Ti-Tambient)